Forum KNX francophone / English KNX forum
Règle de chauffage - comportement bizarre - Version imprimable

+- Forum KNX francophone / English KNX forum (https://www.knx-fr.com)
+-- Forum : Français (https://www.knx-fr.com/forumdisplay.php?fid=3)
+--- Forum : Logiciels libres (linknx, knxweb, pKNyX,...) (https://www.knx-fr.com/forumdisplay.php?fid=10)
+--- Sujet : Règle de chauffage - comportement bizarre (/showthread.php?tid=2429)



Règle de chauffage - comportement bizarre - fma38 - 12/01/2013

Bonjour,

J'ai la règle linknx (pour mon chauffage) suivante :

Code :
<rule id="rule_heating_sdb_rdc">
    <condition type="or">
        <condition type="timer" trigger="true">
            <at hour="6" min="0" exception="no" wdays="12345" />
            <until hour="8" min="0" />
        </condition>
        <condition type="timer" trigger="true">
            <at hour="16" min="0" exception="no" wdays="1245" />
            <until hour="23" min="59" />
        </condition>
        <condition type="timer" trigger="true">
            <at hour="12" min="0" exception="no" wdays="3" />
            <until hour="23" min="59" />
            </condition>
        <condition type="timer" trigger="true">
            <at hour="8" min="0" wdays="67" />
            <until hour="23" min="59" />
        </condition>
        <condition type="timer" trigger="true">
            <at hour="8" min="0" exception="yes" />
            <until hour="23" min="59" />
        </condition>
    </condition>
    <actionlist>
        <action type="set-value" id="heating_setpoint_sdb_rdc" value="21" />
        <action type="set-value" id="heating_setpoint_sejour" value="20" />
    </actionlist>
    <actionlist type="on-false">
        <action type="set-value" id="heating_setpoint_sdb_rdc" value="19" />
        <action type="set-value" id="heating_setpoint_sejour" value="19" />
    </actionlist>
</rule>

Et dans la table log, j'ai ceci :
Code :
2013-01-11 16:00:00  heating_setpoint_sdb_rdc  21
2013-01-11 16:00:00  heating_setpoint_sejour   20
2013-01-11 16:00:24  heating_cmd_sdb_rdc       on
2013-01-11 16:00:29  heating_cmd_sejour        on
2013-01-11 22:24:24  heating_cmd_sejour        off
2013-01-11 23:31:51  heating_cmd_sejour        on
2013-01-11 23:59:00  heating_setpoint_sdb_rdc  21
2013-01-12 08:00:00  heating_setpoint_sdb_rdc  19
2013-01-12 08:00:00  heating_setpoint_sejour   19
2013-01-12 08:00:00  heating_setpoint_sdb_rdc  21
2013-01-12 08:00:00  heating_setpoint_sejour   20
2013-01-12 08:00:00  heating_setpoint_sdb_rdc  19
2013-01-12 08:00:00  heating_setpoint_sejour   19
2013-01-12 08:00:00  heating_setpoint_sdb_rdc  21
2013-01-12 08:00:00  heating_setpoint_sejour   20

Comme vous pouvez le voir, à 16h hier soir, les 2 consignes sont passées à leur valeur confort (20°C et 21°C) ; les radiateurs se sont bien déclenchés.

Mais ensuite, à 23h59, au lieu de repasser en éco (19°C pour les 2 consignes), seule la consigne SDB a été renvoyée, mais avec la valeur confort !

Et ce matin à 8h00, y'a eu un mic-mac, les consignes alternant entre confort et éco.

J'ai eu une coupure sur le matos KNX hier à 20h (bus + la box). C'est certainement ça qui a foutu la merde, mais j'aimerais comprendre pourquoi. Qu'aurit-il fallu faire pour que ça reparte correctement ?

Merci de vos lumières.